One of my biggest customers is a day camp in my home town. There are (4) swimming pools with slides, heaters, etc. Several of the pool motors are 3-phase, 30-amp Delta, 240V units. Prior to last year the motors and heaters for these pools were not GFCI protected. Two weeks before the camp was due to open the local inspector came in to inspect the pool grounding and noticed that these motors and heaters were not properly protected. He would not sign-off on the grounding unless the owner provided GFCI protection for these pools.
That said, while I believe properly protecting the pools is the right thing to do, why did he wait until 2 weeks before the camp was due to open ? Not that $$$ had anything to do with this but the camp gets almost 1000 kids at $4K per kid for 42 days of camp. Do the math and you can understand why the camp owner became irritated when this "gun" was put to his head. This was not a matter of $$$ - it was a matter of timing.
Anyway, at the time the only breaker manufacturer that made 3-phase GFCI breakers was Square D but the camp had no Square D equipment installed. We found these products that we installed and they worked fine and were accepted by the inspector :
www.gfcistore.com
I'm posting this in case any of you have a similar situation for large pool facilities with 3-phase motors.
40-60 Amp Portable ELCI | GFCISTORE