SparkyAdam
- Oregon
- Electrician/Small Business Owner
Hello Forums,
We are building a new Electrical service on an existing building. The existing building was single phase, and they are moving to three phase 208. We are refeeding all the existing single phase panels and are adding a separate three phase panel for a few three phase loads they are adding. This is a total of four panels, three existing single phase and one new three phase panel. The building is becoming a small brewery and they have need of a few three phase circuits for brewery equipment.
The service is a 3-phase 400-amp overhead service, and the service disconnect we are installing is a DG325NRK (pictured below).
The disconnect pictured above needs to feed four separate disconnects and the lugs included are only rated for a max of 2x 300KCMIL wires max. I need to run four 250's out of this. There is not a lot of space on the load side for bigger lugs, so my solution is to use a 2-Sided Insulated Multi-Tap Connector (IPLD250-4 or similar).
What I am thinking of doing is running two wires from the included load side lugs, passing these two wires directly through the multi-tap connector above and taking those wires directly to two of the panels, then using the two open ports of the insulated lugs as a tap to feed the other two panel disconnects.
Something like this image.
This is a bit weird, and I'm not certain this would be code-compliant though I cannot think of what rule it would violate.
Any thoughts?
Any thoughts?