LarryFine
- Henrico County, VA
- Electrical Contractor
I use a solenoid tester for 99% of troubleshooting.
You are correct, there are several things that come into play. It will also depend on what the de-energized conductor is connected to.Although the two conductors separated by insulation can create a capacitive effect, I thought the effect of voltage seen on the wire not connected to power to be caused more through inductance and changing of AC field from the hot wire rather than the capacitive portion
For it to be inductance wouldn't you need a ferrous core involved between conductors? Without the ferrous core you have a capacitor.I witnessed a dead wire show voltage on it while ran within the same conduit of another line side hot switch wire. Or at least the trick tracer beeped on this wire.
I don't understand what you mean by an "open neutral". If it isn't connected to anything it is just a wire.It's an open neutral .
Depends on if the other side of the load is connected to an energized conductor.I don't understand what you mean by an "open neutral". If it isn't connected to anything it is just a wire.
Does one normally megger conductors that are connected to loads? I have never done it.Depends on if the other side of the load is connected to an energized conductor.
Some where in this thread someone asked why you can get bit from the white (neutral) wire. that is what I was referring to.Does one normally megger conductors that are connected to loads? I have never done it.
That was me asking why non-contact sensors wont detect current flowing on the neutral.Some where in this thread someone asked why you can get bit from the white (neutral) wire.
Not a bad overall explanation. But I take issue with one point, that Stray Voltage (typically Neutral-Earth Voltage, NEV) is usually associated with dairies. It is no more common at dairies than at any other farm or rural distribution environment, where metallic neutral runs are long and ground electrodes in the supply system are fewer and farther between. And it can easily occur in residential situations too.That was me asking why non-contact sensors wont detect current flowing on the neutral.
I believe there are a few good answers:
ptonsparky points out open neutral at empty receptacles.
LarryFine points out capacitance changes somehow on its way to earth ground.
Maybe after going thru the load, electrons are too tired to give any more static.
Now I understand your question! Non-contact testers detect voltage, not current.That was me asking why non-contact sensors wont detect current flowing on the neutral.
Can't cows be fitted with insulated booties?But dairies are much more affected by NEV since cows with their four footed stance are more susceptible to voltage gradients in the earth and even small perceived voltages in the earth or to metallic contacts like feed and water troughs will have a severe effect on milk production.
They could. I know of a 3000 head Dairy you could try it out on.Can't cows be fitted with insulated booties?![]()
That would only be 12,000 booties. Or walk the cows through a trough of Flex Seal liquid.They could. I know of a 3000 head Dairy you could try it out on.
When I say inductive I’m referring to a “voltage” being induced from the source wire to the adjacent wire through close proximity just as a transformer does between primary and secondary wires.For it to be inductance wouldn't you need a ferrous core involved between conductors? Without the ferrous core you have a capacitor.
They both have similar but opposite effects. Current leads voltage with one and lags with the other, if you have a circuit for current to flow through anyway.
Can you describe more on what these loads types are and what effect these have? Would the load such as harmonic really need to factored in for the effect ? Perhaps if a current is to travel on second wireYou are correct, there are several things that come into play. It will also depend on what the de-energized conductor is connected to.
Though you may be able to do this with other materials, iron core is the best way as it has the best magnetic properties.The “classic” case of ghost or phantom voltage is caused by capacitive coupling. In a typical case an energized conductor is in the neighborhood of a unconnected neutral conductor. This “neighborhood" physical proximity causes a capacitance between the conductors of ~ 5 to 20 pF per foot. For example, in 20 feet of NM cable (or conducts in same conduit) you could have 200 pF which at 60 Hz gives a capacitive reactance of 13Mohms.
Now the equivalent circuit is a source connected to two resistances (reactances) in series, the first being the virtual capacitor formed by the conductors and the second being the meter (assumed to be connected from the neutral to ground). If you have a typical high-impedance electronic DVM with ~ 10M ohm input impedance you can see half the voltage is dropped across each element which could result in a voltage reading of 40 -60V (assuming 115V source). If you use a solenoid tester, meter with Lo-Z capability, or even old VOM, the meter resistance is so low compared to the Mohm of the virtual capacitor, you get a correct reading (i.e. ~ all the voltage is dropped across the virtual capacitor).
As to inductive coupling, I guess we can argue about semantics, but for inductive coupling to occur, my opinion is you need to have time varying current flow magnetically coupled to a loop(s) which induces voltage via Faraday's law. In the case above, no current is flowing and it is simply an AC circuit formed by two impedances.
single conductor run in a ferrous raceway is an inductor. Not as good of one as a transformer or a solenoid coil with several wraps around a core but it will have more inductive properties than a single conductor in free air has.When I say inductive I’m referring to a “voltage” being induced from the source wire to the adjacent wire through close proximity just as a transformer does between primary and secondary wires.
Also as a not coiled wires also induce a voltage into themselves called counter EMF which resist the direction of current which created it - hence impedance.
Inductors store energy in an electromagnetic field while capacitors store energy in an electro static field
Perhaps there is also a small capacitive effect as well
Open neutral has same voltage potential as the ungrounded conductor trying to supply a load in the circuit on the side connected to the load. The other side is a grounded conductor.That was me asking why non-contact sensors wont detect current flowing on the neutral.
Now I get it. Thank you sir.Open neutral has same voltage potential as the ungrounded conductor trying to supply a load in the circuit on the side connected to the load. The other side is a grounded conductor.
An intact neutral conductor is at same potential as the grounded source conductor, less any voltage drop at the point of measurement when there is current flowing.
If voltage drop is only a volt or so the typical NCVT isn't going to be designed to pick this up and indicate it as "hot"
Very clever. Thank you for sharing this.A somewhat better use for NCVT is checking equipment grounding. If you forgot to connect the EGC to something, particularly with non metallic wiring methods where there is no other conductive path to pick up bonding, A NCVT works pretty good most of the time at indicating that there is no intact EGC to the item being tested as that item will have capacitively coupled voltage on it. It won't be good enough of a capacitor for you to get a shock when you touch it, as long as there is not actual ground fault involved.
Used to have inspectors that held NCVT's up to switch covers or luminaires when doing final inspections, and turn the switch on as it needs to have active load or it won't have any voltage to couple with. If you forgot to bond the switch yoke it will indicate voltage nearly every time. Only had one time that I recall getting a false positive when a luminaire was setting off the NCVT yet we checked things out and the luminaire was bonded properly and even tested with DMM. Had it not set off the NCVT we wouldn't have spent the time verifying it actually was bonded.