Mumbaigirl
- USA
- Electrical Engineer
Hello, I am very new to this:
I have a 440-ton quad compressor chiller unit we are renting and below are the RLA and FLA details:
460V/60HZ
System 1 : Compressor 1: RLA= 180A; Condensor 1 Fans FLA = 2.8A each for 6 fans
System 2 : Compressor 2: RLA= 180A; Condensor 2 Fans FLA = 2.8A each for 5 fans
System 3 : Compressor 3: RLA= 150A; Condensor 3 Fans FLA = 2.8A each for 5 fans
System 4 : Compressor 4: RLA= 150A; Condensor 4 Fans FLA = 2.8A each for 5 fans
System 1/3 : Control KVA = 2.4
System 2/4 : Control KVA = 1.8
Per the cutsheet, RLA for the chiller ONLY is 763, the MCA is 763A and the recommended fuse/circuit breaker rating is 1000A when you run the entire system.
I have an 800A service available (disconnect switch) for this chiller and I am trying to figure out if that will be enough if I run only 3 compressors. (they tell me they need about 300-350ton capacity and not the entire 440 ton):
Assuming I can only run compressor 1, 2 and 3 (they have individual disconnects) , can I calculate the maximum overcurrent protection as :
2.25*180 + 6*2.8 +180 + 5* 2.8 + 150 + 5* 2.8 = 780A + some control RLA = 800 approx. and use my 800A breaker to feed this?
460V/60HZ