The problem I run into is homeowners don't usually buy a 80kW generator instead they get some hot deal on 14kw with a 200 Amp ATS included and want it installed on the entire 320A service.Can't all ATSs be manually overridden to be started, stopped, and/or kept off?
Yes. But the problem with shutting it down under load is starting it back up under load and if it's big enough load the generator may not like that. You would almost want the ATS to go to neutral on shutdownCan't all ATSs be manually overridden to be started, stopped, and/or kept off?
This oneās one of my concerns. I donāt know what wet stacking is. Is that the proper term so o can google.With this being so oversized, she might have problems with the driver "wet-stacking" due to not enough load. Bigger is not always better.
Diesel not running with enough load can run below it's designed running temperature, can lead to unburned fuel and soot passing on through and into the exhaust system. Will reduce efficiency (even more) and likely will shorten life of the engine as well.This oneās one of my concerns. I donāt know what wet stacking is. Is that the proper term so o can google.
Found link on wet stacking.This oneās one of my concerns. I donāt know what wet stacking is. Is that the proper term so o can google.
Thatās a problem too, a lot of automatic transfer switches do not have a neutral position, especially that size.Yes. But the problem with shutting it down under load is starting it back up under load and if it's big enough load the generator may not like that. You would almost want the ATS to go to neutral on shutdown
Seems if they want to save fuel they should have gone with a smaller unit. JMO.
That diesel motor is probably like 75ish horsepower at a minimum.
It still going to suck down the fuel when it is running even if not loaded much. Plus diesel won't store all that long compared to LP or NG but you will want a pretty good supply of it should you have a longer term outage situation.
Do they even have enough "essential" load in the house to load this thing beyond 25% of it's capacity? Load shedding of bigger loads lets you use smaller generator and still be able to run those bigger loads when there isn't much other loading.
She filthy rich, she bought online. probably was asked what size service she has and then they gave her 334 Amp gen. This is her lake house they don't even use it only 3 months out of the year.....Did she give any explanation for getting such an oversized generator? Bigger= more fuel consumption= less run time= end of her world happens sooner.
-Hal
But AFAIK they usually do not automatically transfer to the standby source until there is voltage sensed from that source.Thatās a problem too, a lot of automatic transfer switches do not have a neutral position, especially that size.
The bigger ones have a āgo to neutralā position, and can be programmed to have a time delay for large loads to come to a stop before transferring. The opās problem is it will not transfer back to utility if both sources are dead. Easiest way is to turn off the generator output breaker before restarting.But AFAIK they usually do not automatically transfer to the standby source until there is voltage sensed from that source.
OP's client basically wants a manual transfer switch, so that is likely what I would get them.The bigger ones have a āgo to neutralā position, and can be programmed to have a time delay for large loads to come to a stop before transferring. The opās problem is it will not transfer back to utility if both sources are dead. Easiest way is to turn off the generator output breaker before restarting.
If they were simply misinformed or suckered into buying the large unit maybe suggest they don't install it and instead sell it and get something more suitable for their needs.
Roger, that is correct because the golden rule is an ats will not transfer to a dead bus (source), unless, in the case of Zeniths, the Load Shed option will allow it to transfer to either neutral or utility source depending on 2 or 3 position ats design, when shedding the load.But AFAIK they usually do not automatically transfer to the standby source until there is voltage sensed from that source.