Alwayslearningelec
- NJ
- Estimator
What size conductors are in the raceway? If the conductors are smaller than #4 then 314.28 doesn't applySo these C's don't look like they are sized according 314.28. Referring to larger conduits that look like ~3". I'm assuming the larger conduit will have #4 or larger conductors.
Not sure but I got ya on of they are larger than #4. Is there any relief to sizing conduit bodies with #4 or larger?What size conductors are in the raceway? If the conductors are smaller than #4 then 314.28 doesn't apply
I don't think so.Not sure but I got ya on of they are larger than #4. Is there any relief to sizing conduit bodies with #4 or larger?
(A) Minimum Size.
For raceways containing conductors of 4 AWG or larger that are required to be insulated, and for cables containing conductors of 4 AWG or larger, the minimum dimensions of pull or junction boxes installed in a raceway or cable run shall comply with 314.28(A)(1) through (A)(3). Where an enclosure dimension is to be calculated based on the diameter of entering raceways, the diameter shall be the metric designator (trade size) expressed in the units of measurement employed.
1) Straight Pulls.
In straight pulls, the length of the box or conduit body shall not be less than eight times the metric designator (trade size) of the largest raceway.
Doesn't that get flagged or doesn't the engineer need to approve?Those can be used to pull in the pulling rope or a tru-tape but that's about it. I've seen it a hundred times where guys use C conduit bodies on big pipe to satisfy the 360° rule and they have no idea that they're not code compliant as a pull point.
The inspectors that I know will flag that as not having the required pull points as the C does not qualify as a pull point. Yes, I know we typically pull through more than 360 degrees of bend in the real world.In my experience no one really cares. Most of the time with big conduits you pull through 6, 7, or 8 90's with the pulling machine.
That is a great idea, but why not close them up so you can blow strings without getting to the fitting?Those can be used to pull in the pulling rope or a tru-tape but that's about it. I've seen it a hundred times where guys use C conduit bodies on big pipe to satisfy the 360° rule and they have no idea that they're not code compliant as a pull point.
Looks nice too. I love the fact that they put the covers on during the installation and left them open. I always insisted that my guys do that so the cover is already there.
The guys will pull 500 or 600 mcm through 5+ 90's?In my experience no one really cares. Most of the time with big conduits you pull through 6, 7, or 8 90's with the pulling machine.
Not uncommon. However whenever I did that, I ran the pulling calculations for both the pulling tension and the sidewall pressure. In most cases the sidewall pressure is the limiting factor. Sidewall pressure is the crushing force on the conductor insulation when pulled around the 90s. It is a function of the pulling tension and the radius of the bend in feet.The guys will pull 500 or 600 mcm through 5+ 90's?
Absolutely. A Ultra Tugger can pull about 12,000 pounds.The guys will pull 500 or 600 mcm through 5+ 90's?
Doesn't that do damage to the wires? I thought that was the reason for not using more than 360°Absolutely. A Ultra Tugger can pull about 12,000 pounds.
As long as the scraped sections don't line up or touch the conduit, all is golden! (;Doesn't that do damage to the wires? I thought that was the reason for not using more than 360°
I am talking about the tension on the wire. Certainly could be an issue with smaller wires..... IDKAs long as the scraped sections don't line up or touch the conduit, all is golden! (;
The tension is rarely the limiting factor when pulling large conductors. When I did the pulling calculations, the limiting factor was always the sidewall pressure.I am talking about the tension on the wire. Certainly could be an issue with smaller wires..... IDK
. We would often use 3 or 4' length of 6" wireway as an LB because it gave you more room and was cheaper than the correct LB.