Trying to understand if code allows you to eliminate one electrode (rod) if you have a UFER installed. Excerpts are from the 2020 NEC...Some background our utility provider requires a rod at the meter. All our water services are copper and all new residential builds require a UFER. So "present - 250 .50" would be Rod, Water, UFER.
(underlines by me
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system.
250.53 Grounding Electrode System Installation.
(2) Supplemental Electrode Required.
A single rod, pipe, or plate electrode shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). The supplemental electrode shall be permitted to be bonded to one of the following:
Exception:
If a single rod, pipe, or plate grounding electrode has a resistance to earth of 25 ohms or less, the supplemental electrode shall not be required.
(D) Metal Underground Water Pipe.
If used as a grounding electrode, metal underground water pipe shall meet the requirements of 250.53(D)(1) and (D)(2).
A metal underground water pipe shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). If the supplemental electrode is of the rod, pipe, or plate type, it shall comply with 250.53(A).
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(3) Concrete-Encased Electrode.
So as mentioned, our utility requires a rod at the meter and in reading the code both water and rod type electrodes shall be supplemented by an additional electrode. Question - can the UFER be the additional required electrode for both the rod and water present or is an additional supplemental electrode required for each (water and rod).
(underlines by me
Exception: