mjcasey
- Fairfield Iowa
- Electrician
I have 4 outside receptacles....all protected by a 20 amp GFCI CB. They all have your standard weatherproof cover.
The inspector wants extra heavy duty IN-USE covers in every location. I objected......siting the exception to 406.9:
Exception: 15- and 20-ampere, 125- through 250-volt receptacles installed in a wet location and subject to routine high-pressure spray washing shall be permitted to have an enclosure that is weatherproof when the attachment plug is removed.
All 15- and 20-ampere, 125- and 250-volt nonlocking-type receptacles shall be listed and so identified as the weather-resistant type.
Do I have a valid stance?