400 amps underground service 280' from transformer to meter

The load calculation has nothing to do with the length of the conductors. Are you trying to do a voltage drop calculation?
 
Hard to say without knowing any of the loads, but most of the time 350 MCM AL would cover it. Something like a big on demand water heater or resistive pool heater or a ton of electric heat might make me go bigger.
 
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
 
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
We have had to provide and install the underground from a pad mount to the service equipment for commercial services for a long time. The only think the utility does is terminate at the transformer. Recently they have stated to require that for dwellings too.
 
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
the other way around for me. The idea of the Poco pulling conductors to the meter socket baffles me, I think I've seen it once in
25 years!
 
IF your calculated load is actually 350 amps (rare on residential), to maintain a 3% voltage drop you would need parallel 300 kcmil AL and, if you don't reduce the neutral, it would take a 3" PVCconduit (assuming there is some Sch 80)
 