Fire Alarm Conduit

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
When an initiating(pull station) and notification(speaker strobe) are directly underneath each other like this do you run both circuits in same conduit?
I have always figured it like that and is allowed by code.


1736888348579.png
 
Generally, yes. Manufacturers may publish their own charts which tell you what circuits can run together. For Siemens, it's almost everything, except the output from their ZAM-180 amplifiers; those are not current limited.
 