Installing busduct or cablebus for padmounted transformer
rotmgbetter
Houston, Texas
Researcher
I have a customer owned transformer that will be located right outside of the building and the switchgear will be right across the wall in the inside of the builidng. This will be a 480V, 4500 amp service on the secondary.
The main goal is to decrease cost for having to jackhammer the interior of the building and pulling the wire.
First of all, is cablebus and busduct exclusive for the substation style transformers with flanges and throats or is there commercially available solutions to convert a padmounted transformer so it is compatible with cablebus/busduct?
Secondly, will there be any cost advantage at all to having an overhead cablebus/busduct going directly into the switchgear vs just normal underground conduits?
Thirdly, for a run that is less than 10 feet, would cablebus or busduct be more economical?
I guess one more question, is it any cheaper to have the underground conduits pop out while still outside, run along the wall and then enter from overhead.
This is pretty common.
One job had a cable tray run up the side of the building. The customer had a picture taken of the brick wall which was sent to a 'sign' company to be turned into a decal for the tray cover, 10 yrs later it is still camouflaged.
In that scenario, how does the derating and ampacity work? Would you follow the derating for 3 or more conductors in a conduit + ampacity of buried insulated conductors or is there a critical length of conduit run where under that length you can follow the ampacity for in free air?
Because the run began in underground conduits and finished in indoor conduits a choice was made to not have transitions, the conductors were sized as if the entire run was in conduit not open air.
Anyone know if the additional cost of a bus duct will offset the labor cost of installing 12 conduits at 500 kcmil with 4 strands in each if it is a short run.
This doesn't seem to be a common approach but one of the contractors on the project is proposing this to save money.
Can you use bus duct as service entrance conductors?
I know they have a SCCR, but it that not based on the bus duct being protected with an OCPD with that rating and will clear the circuit in 1-3 cycles?
What is the bus duct X/R test value to evaluate if it over of range?
Consider a substation-type transformer with an air terminal compartment on the secondary - you could just go through the wall into the ATC.
Can the utility trans primary OCP satisfy 368.17(A)?
I don't know, I haven't looked yet.
But, utility primary side protective devices are typically intended to removed faulted equipment from their grid. They are all but never sized to meet NEC protection requirements.
368.1 says service entrance bus duct is allowed.
368.17 outlines OCPD requirements for bus duct used as feeders or branches.
There is nothing about service entrances, so 230.91 should still be applicable.
Not disagreeing...just have never seen this done.
The UL white book has a line that states something to the effect that all components used for SE must carry that label.
There must be some specific testing needed to get this label.
Thanks for looking at the topic.
We make an elevated concrete pad with a channel made on the top surface to route the secondary conductors through with an opening on the side where we mate the pad with the cablebus flange. The cablebus sits on supports a few inches above grade on its way to the required disconnect immediately on the inside of the building.
Can you provide which cable bus brand you use? For the ones I've been talking to seen it is cheaper to go the tranditional conduit + cable route.
Also, can you explain what you mean with a channel made on the top surface? Would this look like a u channel made of concrete? Let's say you have a cable bus that is arbitrarily 12"x24", how big would this channel be?
We've used MP Husky and Superior Cable Tray.
The channel is made the same dimension as the cablebus flange. A plate is put on top of the exposed channel from the cablebus flange to the edge of the transformer to protect the conductors. The conductors lay in the concrete channel between the cablebus flange and the bottom entry of the pad mount transformer.
I'm talking to superior cable tray right now. Wht are the pros and cons of the two companies?
I guess for longer runs this makes sense but if the transformer is right next to the wall (the pad is 3 ft from the wall), do you think it is better to get a custom flange on the top of the pad mount transformer?
MP Husky and Superior are competitors. Competition is good. They are similar, although Superior will do custom stuff.
You might be able to get a custom opening on the side of a pad mount transformer, but I do not suggest top due to potential rain intrusion.
Short runs are not likely worth it unless the smaller profile is helpful.