DLO - Diesel Locomotive Cable
Structure engineer needs to involve if EC suspend cable with unistrut & cable clamp/strap from structure above?
I guess that depends on where you're hanging it. In a plant there might be someone who cares how it's suspended but on a construction site no.
With very high current and assuming that the strut and strut strap are ferrous, I can see a potential for inductive heating at the support point assuming there is only a single AC conductor run through the porcelain. Probably not a real world issue unless the current on the conductor exceeds 400 amps.
I'm pretty sure someone makes a strap/insulator that would fit the 3 cables in one strap. Besides the theoretical issue you've mentioned I've never seen a problem in the field even when the conductors are individually strapped.
I have seen this arrangement on 5kv cables where the straps were noticeably warm, but not hot enough to damage. Not sure what the current on the 5kv cables was.
I saw it once in a strange situation.
Battery inverter conductors left a gutter to a battery box at individual KOs with bushings or something.
Well the inverters allowed a lot of ripple current onto those DC wires, a couple hundred amps DC and a couple hundred amps ripple as well as measured by Fluke amp clamp.
Those gutters about wanted to jump off the wall when the loads got heavy, or the sun got high (they were also charging). The buzzing and rattling was intense.
The customer just lived with it like that, it was a separate shed. Still like that afaik.
I've run miles of these cables for load bank testing and the last thing you want to do is try and suspend this stuff in the air if you can avoid it.
Do you know to support , secure these cables when run them between floors inside a chase vertically? any special canle hood for large cable size?
Best way to support them vertically is not to have drops longer than a few feet. You could use Kellems, but check with the mfg for the cable pull ratings. When I've had to run some up a couple of levels, we use the stairs (being careful not to block egress paths/etc).
I've read back in the thread and can't tell if this is short- or long-term temporary, or permanent, that makes a huge difference to the question "how to support". So do the local conditions.
Oh, and the standard reminder- DLO is not an NEC cable type. You might be using dual-rated type RHH/RHW, type W, etc.... calling all fine-strand cable "DLO" is not accurate.