Jw0307
- California
- Electrician
Would a receptacle in a upper cabinet of a kitchen for a microwave need a GFCI? The outlet is with in 6’ of the sink but it is not servicing the counter top and it’s not along the counter top
I would say no.Would a receptacle in a upper cabinet of a kitchen for a microwave need a GFCI? The outlet is with in 6’ of the sink but it is not servicing the counter top and it’s not along the counter top
Thank youI would say no.
The building is going off of 2019 codeWhat code cycle are you under? It may make a difference.
Ron
I assume you mean the 2017 NEC as there is not 2019 NEC.The building is going off of 2019 code
No. There is a upper cabinet specifically for the microwave above the counter and the outlet is inside of that sectionIs the 6' a straight line or the path a power cord would have to take?
is
is
No. The upper cabinet is specifically for the microwave above the counter and the receptacle is placed inside of that section. If that makes senseIs the 6' a straight line or the path a power cord would have to take?
is
Is there a door in front of the microwave?No. There is a upper cabinet specifically for the microwave above the counter and the outlet is inside of that section
For the purposes of this section, when determining distance from receptacles the distance shall be measured as the shortest path the cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or passing through a door, doorway, or window.
I would think that, if a cabinet door qualifies as a door, then an open cabinet front would qualify as a doorway.Is there a door in front of the microwave?
I wouldn't and there was never an intent for a cabinet door to count for this measurement, that is why that language is no longer in the code. Removing the door language made any receptacle under the sink cabinet subject to the GFCI rules. There was extensive debate after the 2017 was published and in the 2020 the language was changed to.I would think that, if a cabinet door qualifies as a door, then an open cabinet front would qualify as a doorway.
For the purposes of this section, when determining the distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a window.
How the previous Forman had it ran was based off the plans as that plug is the second small appliance circuit and it’s dedicated. If you mean by plugging micro into GFCI below then they would need to cut the bottom for the cord to go thru which they do not want to doThat's pretty darned close, and it's the appliance, too, not just the receptacle.
Can you feed it through the GFCI receptacle below it?
No, I meant the two receptacles on one circuit. Your way would need a second GFCI.How the previous Forman had it ran was based off the plans as that plug is the second small appliance circuit and it’s dedicated. If you mean by plugging micro into GFCI below then they would need to cut the bottom for the cord to go thru which they do not want to do
We would be able to fish a wire down to the lower GFCI and connect them that way. So your saying how it is now a GFCI would be needed in that location above?No, I meant the two receptacles on one circuit. Your way would need a second GFCI.
OP has the location listed as "California" so he is correct saying it's "going off of 2019 code", but you are also correct because the 2019 CA Electrical Code is based off of the 2017 NEC. I agree with your interpretation and if I was the inspector for this job, I would have called it out too.I assume you mean the 2017 NEC as there is not 2019 NEC.
210.8(A)(7) in the 2017 will required GFCI protection for this receptacle because it is within 6' of the sink.