bcl
- Garden Ridge, TX
- Electrician (Owner/ Operator)
Recently was handed a set of prints for estimating. (20) EV chargers fed from a 400 amp/ 480v busway. They have designed such that each individual charger has its own 15kVA transformer (480/240). This designed seemed to me to be sort of silly. Why not just install a larger transformer at the beginning of the circuit and run a larger busway. The labor and material to install 20 individual transformers (and hang them 20' in the air!) seems so much more than having a transformer at the beginning of the circuit.
While you're reading this, I'm also having this issue that can't get a fast enough answer back from suppliers...and haven't installed busway in a long time. Is there a ball-park for how much you expect to pay per foot for 400 amp copper busway? Here are the details I have:
3 phase, 3 wire with internal ground (not grounded enclosure), 400 amp, 480v
The run is about 250 feet, with the final 100 feet installed as bus-plug with (20) 30 amp plugs for EV chargers.
I'm good on labor and material count, but everyone says "they'll get back to me" on price, and I'm looking for at least a ballpark I can give the GC now.
Thanks in advance!