johnnydn
New User
- Oakland, CA
- Junior Electrical Design Engineer
I am having trouble interpreting the code which requires GF protection on service disconnects. I've read from different online resources that this is only a requirement for 480/277V but not 120/208V systems. My confusion is where does the code delineate which voltage systems are applicable and which are not? Does the Utility (CA in my case) have special exceptions which trigger this 480/277V only or is there a code section that articulates this delineation?
Taken from 2017 NEC:
230.95 Ground-Fault Protection of Equipment.
Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. The grounded conductor for the solidly grounded wye system shall be connected directly to ground through a grounding electrode system, as specified in 250.50, without inserting any resistor or impedance device.
The rating of the service disconnect shall be considered to be the rating of the largest fuse that can be installed or the highest continuous current trip setting for which the actual overcurrent device installed in a circuit breaker is rated or can be adjusted.