As per this code rule, if any ungrounded conductors are increased in size for any reason, other than as required at 310.15 (B) or 310.15 (C) wire type equipment grounding conductors, if installed, shall be increased in size proportionately to the increased and circular area of the ungrounded conductors.
Exception: equipment, grounding conductors shall be permitted to be sized by qualified person to provide an effective ground fault current path in accordance with 250.4 (A)(5) or (B)(4)
My question: given the allowed exception, what is the easiest way to determine if a egc is of sufficient size. After watching a Ryan Jackson video on the subject, 5 times the current rating on a breaker and over is enough current to trip the breaker in sufficient time.
So how would you determine the correct egc size in a scenario where you’ve upsized for voltage drop ( let’s say pole lights in a parking lot).
20 amp pole lights
Upsized ungrounded conductors to 8 awg
Lets say 500’ to the farthest light.
How would you size the ground and what formula if any would you use?
20 amp pole lights