Its only a issue with very long runs, say large parking lot lights or long path lighting If you play around with the numbers you could see situations where the available fault current is not enough to trip a breaker or it would take hours for either the breaker to trip or the weakest link in the equipment ground fault path burns out.
For example a large corporate campus with 480 service has a single phase step down transformer 8000A available fault current at the 120/240 secondary of the transformer,
Then a 500' run of #4 AL to a outdoor lighting panel out in a parking area,
then 1500' run of path lights on #8 AL and you pulled a #8 AL equipment ground.
Say the lights are really efficient LED so voltage drop is not an issue, they also are wired 240V to reduce voltage drop,
the #8 AL direct burial cable is on a 2-pole 40A breaker.
Now say we have a bolted fault to equipment ground at the last light pole.
The available fault current line to ground is something like 33 amps.
Arguably a #8AL EGC could carry that fault current all day long, or until the fault burns up and opens.
For example a large corporate campus with 480 service has a single phase step down transformer 8000A available fault current at the 120/240 secondary of the transformer,
Then a 500' run of #4 AL to a outdoor lighting panel out in a parking area,
then 1500' run of path lights on #8 AL and you pulled a #8 AL equipment ground.
Say the lights are really efficient LED so voltage drop is not an issue, they also are wired 240V to reduce voltage drop,
the #8 AL direct burial cable is on a 2-pole 40A breaker.
Now say we have a bolted fault to equipment ground at the last light pole.
The available fault current line to ground is something like 33 amps.
Arguably a #8AL EGC could carry that fault current all day long, or until the fault burns up and opens.