Splicing sub panel wires to main feeders in panel

Merry Christmas

mikee0101

Member
Location
South Carolina
Occupation
Maintenance
Looked up codes but still confused whether this allowed or not .Saw the 40% rule . But have always put sub panels on its on breaker .This is on a residential house built in the 60's ?
 
What is your question?

Do you have a separate panel fed without a breaker from a splice on the service conductors? Is this separate panel located next to the main panel? Is this separate panel supplied with separate ground and neutral?

Can you post a photo?

-Jonathan
 
What is your question?

Do you have a separate panel fed without a breaker from a splice on the service conductors? Is this separate panel located next to the main panel? Is this separate panel supplied with separate ground and neutral?

Can you post a photo?

-Jonathan
 
Trying to post picture but can't find a way to pull from gallery. It is a 200 amp panel with wires going to 150 amp sub panel . Wires were skinned and some type of split bolt added and then just regular black electrical taped .
 
This is the main panel with wires spliced going to the sub panel. I always run separate breaker for the sub . Plus that kinda is beyond the 75% rule .
 

Attachments

  • 20250320_165932.jpg
    20250320_165932.jpg
    1.1 MB · Views: 27
  • 20250320_165927.jpg
    20250320_165927.jpg
    965.9 KB · Views: 27
Then nothing wrong with it in general, other than the devil of some details. What you have basically becomes a 230.40 exception #2 install, done every day in commercial work. Details of concern would be the length of the service conductors, whether that second panel has a service disconnecting means, and details of the grounding electrode conductor connection.
 