PPE level / ARC flash suit
mackotis
NJ
My company recently took our PPE Arc flash protection (level 4) suit away and informed myself and another licensed electrician in NJ that we can't work on high voltage electrical equipment until we have ARC flash suit certification to even wear the equipment. Is this a NFPA requirement or just my company being over cautious ?
It's an OSHA regulation. NFPA 70E gives guidelines.
NFPA 70E, and OSHA, require a worker to be trained in order to be considered Qualified.
Retraining must be done every 3(?) years.
Each company is allowed to decided what the training is, how often it occurs, and if testing is required. Many companies want to see hands on training of tools, test equipment and PPE.
It's one thing if your company had taken away the level 4 suit and simply said you can't work on anything requiring that level until you get certification. But it's entirely different thing if your employer took the safety equipment away and tells you to still work on it.
Thanks Roger . I see conflicting information .Some say its not a requirement but a suggestion and other info say yes its requirement of OSHA
It's not a problem for sure .More training and certifications are always welcome . The question was is it a requirement or just a recommendation?
It is a basic requirement to be qualified.
It is up to the company to decided what the qualified requirements are.
it's not a specific requirement in NFPA 70E. Seems dumb to take away PPE. Any energized work should require an Energized Work Permit anyway.
They could just tell you no live work until training is completed.
NFPA 70E requires that workers exposed to electrical hazards have proper training and use the right PPE, but it doesn’t say you need a special certification just to wear an arc flash suit. Many companies add their own rules for safety and liability reasons, so your employer may want documented training before letting you work on high-voltage equipment.
All the training in the world won't stop you from getting killed if you don't use the PPE and training you received. Just had a local death of a very experienced lineman that made contact in a large pad-mount while prepping for pulling in a new set of conductors. Not sure of the details only what the news was reporting.