I need a bit of advice.
Had to go and wire up a replacement of an electric furnace. The original unit was connected to a 2p 60 Amp breaker, with a 60 Amp no fuse disconnect adjacent to it ( when I arrived all that was there from the old install was the disconnect and whip, no further info on the old unit).
The new unit is a 15kW Trane unit with the heating element divided up into to 2 circuits one at 60 Amp for 2 sets of elements ( including the control circuit and blower), the other at 30 Amp for the 3rd set of elements.
My problem is this: The service panel (located in a closet on the other side of the wall from the furnace) is bolt on GE panel. The ONLY 2 "stabs" left in the panel both have the bolt holes stripped! My options are these: 1 ) locate a GE 2p80 bolt on, use #4 conductors to the furnace, and "polaris tap" them in the furnace junction box to feed each of the 2 OEM breakers. 2) find a new GE interior for the panel. 3) find (if they exist) 2 GE bolt on duplex breakers to give me the space to use a standard 2 pole breaker for the second furnace furnace circuit.
Is there any reason why option #1 cannot be used? The "tap" conductors can be #6, and less then 3 feet long). Do the breakers I mentioned in option 3 exist? I know siemens makes this type of breaker, and I think eaton does too for the bab series panels. Due to the potential lead time, cost and possible lack of availability, I am thinking option #2 is not really practical unless it is my only option.
Any thoughts or ideas??? This is a condominium, and the closet is tight for space, as is the mechanical closet
Howard
Had to go and wire up a replacement of an electric furnace. The original unit was connected to a 2p 60 Amp breaker, with a 60 Amp no fuse disconnect adjacent to it ( when I arrived all that was there from the old install was the disconnect and whip, no further info on the old unit).
The new unit is a 15kW Trane unit with the heating element divided up into to 2 circuits one at 60 Amp for 2 sets of elements ( including the control circuit and blower), the other at 30 Amp for the 3rd set of elements.
My problem is this: The service panel (located in a closet on the other side of the wall from the furnace) is bolt on GE panel. The ONLY 2 "stabs" left in the panel both have the bolt holes stripped! My options are these: 1 ) locate a GE 2p80 bolt on, use #4 conductors to the furnace, and "polaris tap" them in the furnace junction box to feed each of the 2 OEM breakers. 2) find a new GE interior for the panel. 3) find (if they exist) 2 GE bolt on duplex breakers to give me the space to use a standard 2 pole breaker for the second furnace furnace circuit.
Is there any reason why option #1 cannot be used? The "tap" conductors can be #6, and less then 3 feet long). Do the breakers I mentioned in option 3 exist? I know siemens makes this type of breaker, and I think eaton does too for the bab series panels. Due to the potential lead time, cost and possible lack of availability, I am thinking option #2 is not really practical unless it is my only option.
Any thoughts or ideas??? This is a condominium, and the closet is tight for space, as is the mechanical closet
Howard