We have a customer that has 120240 3ph4w service and they just got a new generator. The customer apparently told sales all the Hvac and shop equipment operate in 3phase. The generator was installed but During start up it's determine the Hvac isn't 3phase but single phase 240 and the shop doesn't necessarily operate their equipment full time so.the high leg at generator doesn't work unless some is working the equipment. Apparently the generator does not operate well if all 3phases are not used efficiently and will damage generator. I suggested putting the hvac 240v 1ph equipment and spread all 4 Hvac condenser and air handlers on 1phase 240 but using the high leg. Anyone see a problem with this approach? Or add some type of 208v resistive load using on highleg to keep generator running efficiently during outage.