petersonra
- Northern illinois
- Semi-retired engineer
Someone made a rule and whatever standards body is in charge of such rules voted it in. The same way we got afcis.
Right again, I see it now 250.122 (E) flexible cord and fixture wire it has to be the same size as the ungrounded conductors if its 10 AWG or smaller. If the ungrounded conductors in the cord are larger than 10 AWG they can follow the table.Only if the ungrounded conductors are also 10 AWG. If they are 12 AWG the EGC doesn't need to be any larger than the ungrounded conductors.
Yeah thats interesting, 210 covers branch circuits which in my mind is permanent building wiring that ends at an 'outlet'.Of course overcurrent protection for the 5/20R receptacles here is another thing,
For a portable generator the frame should be bonded at the factory to one of the leads designated as a 'grounded' conductor even if its not connected to earth. Though I have seen people un-bond them when using them as a home backup.and good chance the EGC is floating at the generator anyway so all the EGC does is tie the grounding pins of the receptacle to the generator frame, it will almost never be needed to clear a ground fault
Most I have encountered are usually not bonded, and in more recent years even have labeling that states they are not bonded.For a portable generator the frame should be bonded at the factory to one of the leads designated as a 'grounded' conductor even if its not connected to earth. Though I have seen people un-bond them when using them as a home backup.
Yeah I think your right since Article 250 mentions flexible cords in several places.
Also I guess a manufacturer can never know what the branch circuit OCPD of a cord is.
A cord under the NEC is really a kind of 'tap' in a sense.
I see these Y adapters that go from a 30A on the generator to four 20A cord caps,
I am sure they are intended for just generators but I have seen them used creatively.
so any cords plugged into this are on a 30A breaker; then 250.122 will not line up as it would need a 10 EGC;
I have an adapter I made up, L14-30P to 6-20R, that I use with my portable generator sometimes.View attachment 2577002
More horrors, drop shipped from overseas.
Not nearly as bad as most of them. At least this has one female end!View attachment 2577002
Interesting thought, and you're right that GFCI protection changes the game a bit. However, full-size EGCs are still required mainly due to code compliance (like NEC) and safety redundancy. GFCIs trip quickly, but in rare edge cases—like a failed GFCI or if it's bypassed—the EGC becomes the last line of defense.If the cord set has a permanent inline GFCI that can not be removed without cutting it, why couldn't we have something like 10/2 +16/1 or 12/2+16/1?
Cord sets are not intended for permanent installation and having a full size EGC essentially capable of indefinitely serving as "neutral" through a ground fault into case seems silly. Since you can buy 16 AWG extension cords, 16AWG copper or perhaps 16 CuAl clad would seem adequate for mechanical strength purpose while serving enough conductivity to allow GFCI to work.
The reduced weight without compromising on performance is a big plus.
I believe extension cords are outside the purview of NEC. You could have an extension cord attached to the wall with make shift receptacle going all the way to a window A/C but its not part of wiring. If the extension cord's plug is not plugged into the receptacle when the inspector arrives, I don't believe they have any say on it. It's art decora.Interesting thought, and you're right that GFCI protection changes the game a bit. However, full-size EGCs are still required mainly due to code compliance (like NEC) and safety redundancy. GFCIs trip quickly, but in rare edge cases—like a failed GFCI or if it's bypassed—the EGC becomes the last line of defense.
Also, full-size grounds ensure low impedance paths back to the source during faults, which helps breakers trip fast in non-GFCI scenarios too. Even though it might seem overbuilt, it’s really about covering all possible failure modes, especially since extension cords are so often misused.
But yeah, from a pure engineering standpoint, I see your point—there's probably room for weight and material optimization with more nuanced standards.
BOSCH makes a version of something like this which splits a dryer outlet into two 15A 240v outlets but each 15A receptacle is fused. It's meant specifically for using their washer which runs on 240v.View attachment 2577002
That situation can be pushing it to some degree as to whether the cord is being used for permanent wiring of the structure. Window AC can possibly be considered temporary, but even then don't be concealing the cord inside walls, ceiling, etc. or you are still pushing it as being permanent wiring of the structure.You could have an extension cord attached to the wall with make shift receptacle going all the way to a window A/C but its not part of wiring.
It's an extension cord that is stored in the drop ceiling for maintenance useThat situation can be pushing it to some degree as to whether the cord is being used for permanent wiring of the structure. Window AC can possibly be considered temporary, but even then don't be concealing the cord inside walls, ceiling, etc. or you are still pushing it as being permanent wiring of the structure.