Is panel replacement in order, I think so?

I'm not so interested in the corrosion at that level,
but why it corroded to that level. Cleaning up some terminals can do wonders.

But why ? Humidity, leaks, insects, rodents, plumbing, toxic drywall sulfur, gases from the ground?

No 30-year-old panel should look like that.
I've seen a lot of similar panels.
Could be they didn't run a dehumidifier in the basement (it would get very muggy there in the Midwest).
Locally, it's all EMT, so pipe condensation is an issue in panels, since they're all below ground level and all condensation leaks down into them. But high ambient humidity would also cause that.
 
  • Like
Reactions: J2H
I've seen a lot of similar panels.
Could be they didn't run a dehumidifier in the basement (it would get very muggy there in the Midwest).
Locally, it's all EMT, so pipe condensation is an issue in panels, since they're all below ground level and all condensation leaks down into them. But high ambient humidity would also cause that.
That’s good to know, that this thing is pretty typical for the area, and you have not seen it cause any disasters.
 
There is no way to clean dirty water contamination from inside of a breaker, so those need to be replaced if submerged. Panel bussing can be cleaned, but it might not be worth it. Steel enclosures can be treated like any other steel object.
Te: underwater recovery. I found this after Katrina, pretty useful if you have to justify your actions.

 