Is panel replacement in order, I think so?
I'm not so interested in the corrosion at that level,
but why it corroded to that level. Cleaning up some terminals can do wonders.
But why ? Humidity, leaks, insects, rodents, plumbing, toxic drywall sulfur, gases from the ground?
No 30-year-old panel should look like that.
I've seen a lot of similar panels.
Could be they didn't run a dehumidifier in the basement (it would get very muggy there in the Midwest).
Locally, it's all EMT, so pipe condensation is an issue in panels, since they're all below ground level and all condensation leaks down into them. But high ambient humidity would also cause that.
  • Like
Reactions: J2H
That’s good to know, that this thing is pretty typical for the area, and you have not seen it cause any disasters.
If there’s possibly a service pipe leading outside, they might not duck sealed it and condensations get in from outside
Yes, are correct it was not duct sealed, which I did. But it’s probably too late.
I agree
Most likely leak in service entrance conduit or deteriorated insulation on service entrance conductors
Brings rain water to panell
There is no way to clean dirty water contamination from inside of a breaker, so those need to be replaced if submerged. Panel bussing can be cleaned, but it might not be worth it. Steel enclosures can be treated like any other steel object.
Te: underwater recovery. I found this after Katrina, pretty useful if you have to justify your actions.
  • Like
Reactions: J2H