hhsting
- Glen bunie, md, us
- Junior plan reviewer
Can one install stranded bare copper as grounding electrode conductor or not? Electrican says they dont make #1/0 awg copper.
Yes, generally speaking.Can one install stranded bare copper as grounding electrode conductor or not?
They make 1/0 copper, but maybe not bare 1/0 copper. But so what? A GEC is not required to be bare, just allowed.Electrican says they dont make #1/0 awg copper.
Used lots of bare 1/0, 2/0, and 4/0 bare copper for underground industrial grounding systems.Yes, generally speaking.
They certainly make it, just probably not a stock item at many supply houses.Electrican says they dont make #1/0 awg copper.
From context, what the OP meant was that they supposedly don't make bare #1/0 solid copper, so the electrician wants to use bare #1/0 stranded copper.Electrican says they dont make #1/0 awg copper.
That's the way I read the question. It can be stranded even if it is bare.From context, what the OP meant was that they supposedly don't make bare #1/0 solid copper, so the electrician wants to use bare #1/0 stranded copper.
Cheers, Wayne