Alwayslearningelec
- NJ
- Estimator
ThanksMinimum Circuit Ampacity
That number can be used to size the circuit conductors even if the OCPD is sized larger than the conductor ampacity.Thanks
Probably a typo on your end and o don’t have my book but it would have to me equal or greater to the MCA so 159.4That number can be used to size the circuit conductors even if the OCPD is sized larger than the conductor ampacity. So in your example you could use #1/0 which is rated for 150 amps and a 175 amp OCPD.
Oops you're correct I read the FLA. I'll correct it thanks.Probably a typo on your end and o don’t have my book but it would have to me equal or greater to the MCA so 159.4
Somebody needs to be flogged for that(if you didn't know, ampacity is not allowed in Scrabble)