MCA's

That number can be used to size the circuit conductors even if the OCPD is sized larger than the conductor ampacity. So in your example you could use #1/0 which is rated for 150 amps and a 175 amp OCPD.
Probably a typo on your end and o don’t have my book but it would have to me equal or greater to the MCA so 159.4
 
Right. Wire and other circuit components must be rated for at least the MCA, and the breaker ratting must not exceed the MOP.
 