GAK
- Western South Dakota
- EC
Does a 6 foot LNFC whip from an AC disconnect to the condenser need to be supported or secured? .
No, as long as it doesn't exceed 6'. 356.30Does a 6 foot LNFC whip from an AC disconnect to the condenser need to be supported or secured? .
I'm not looking ant the NEC right now but isn't that only for luminaires?No, as long as it doesn't exceed 6'. 356.30
Ron
It seems that 356.30(4) does mention luminaires. I stand corrected.I pointed to 356.30(1). Inspector replied that it only applies to luminaries.
The inspector needs to learn how to read the language in the code book.I pointed to 356.30(1). Inspector replied that it only applies to luminaries.
356.30 Securing and Supporting.
Type LFNC shall be securely fastened and supported in accordance with one of the following:
(1) Where installed in lengths exceeding 1.8 m (6 ft), the conduit shall be securely fastened at intervals not exceeding 900 mm (3 ft) and within 300 mm (12 in.) on each side of every outlet box, junction box, cabinet, or fitting. Where used, cable ties shall be listed for the application and for securing and supporting.
(2) Securing or supporting of the conduit shall not be required where it is fished, installed in lengths not exceeding 900 mm (3 ft) at terminals where flexibility is required, or installed in lengths not exceeding 1.8 m (6 ft) from a luminaire terminal connection for tap conductors to luminaires permitted in 410.117(C).
(3) Horizontal runs of LFNC supported by openings through framing members at intervals not exceeding 900 mm (3 ft) and securely fastened within 300 mm (12 in.) of termination points shall be permitted.
(4) Securing or supporting of LFNC shall not be required where installed in lengths not exceeding 1.8 m (6 ft) from the last point where the raceway is securely fastened for connections within an accessible ceiling to a luminaire(s) or other equipment. For the purpose of 356.30, listed liquidtight flexible nonmetallic conduit fittings shall be permitted as a means of support.
This is poorly written section. (1) covers everything and (2) through (4) should be deleted.Here's the four different scenarios. In (2) the 6' dimension applies to luminaries, (4) the 6' dimension only applies above a ceiling.
You could leave "Securing or supporting of the conduit shall not be required where it is fished" and incorporate it into (1).(1) covers everything and the rest is totally unneeded.
Did you mean where it exceeds 6 feet?The inspector needs to learn how to read the language in the code book.
356.30(1) applies to all installations where the length of the LFNC does not exceed 6'.
For 6' or less, no support is needed no matter what its function. This rule dates back to when LFNC came into the code and could not be used in lengths over 6' and no support was required.Did you mean where it exceeds 6 feet?
For a HVAC whip 6 feet or less I'd say it falls under 'at terminals where flexibility is required' so a strap at 3 feet.
I see but does 356.30 item (1) not only apply if the whip 6 feet or more?For 6' or less, no support is needed no matter what its function.
No. 356.30 says in effect "choose one". I choose (1). If the length of the LFNC is under 6', then (1) imposes no securing requirements. So no securing is then required.I see but does 356.30 item (1) not only apply if the whip 6 feet or more?
(2) covers fishing in arbitrary lengths, which is not covered by (1).(1) covers everything and the rest is totally unneeded.
But Item one says "Where installed in lengths exceeding"No. 356.30 says in effect "choose one". I choose (1). If the length of the LFNC is under 6', then (1) imposes no securing requirements. So no securing is then required.
Cheers, Wayne
356.30(1) is the only part of 356.30 that imposes an affirmative requirement. All of the other sections remove/relax/clarify that requirement in certain cases. So as 356.30(1) does not impose any requirements on lengths not exceeding 6', 356.30 imposes no requirements in that case.But Item one says "Where installed in lengths exceeding"
Yeah, the "one of the following" wording is weird. I think they really mean "all of the following". But that doesn't change anything for my argument.Item 3 says 'Horizontal runs' so can I pick item 3 if I dont have a Horizontal run?
Yeah I never read it very closely it is a bit odd the wording, I think I have been dinged on a condenser whip item based on item (2) installed 'where flexibility is required'.Yeah, the "one of the following" wording is weird. I think they really mean "all of the following". But that doesn't change anything for my argument.
Basically, if you have an unsupported length of LFNC that is 6' or under, you can not point to any specific sentence in 356.30 that is violated.
Cheers, Wayne
And some manufacturers instructions are specific about stuff like ring crimps vs spades and stranded wire.Section 26
D) Use flexible electrical conduit between all motors, rotating or reciprocating equipment and pipes and ducts and electrical conduit that are connected to such equipment.
Occupant vibration criteria shall be based on guidelines recommended in ANSI/ASHRAE Standard ....
Is flexibility at most HVAC required or just convenient? Add: I see Don sees it as convenient.Did you mean where it exceeds 6 feet?