Finally got to the correct site. Verified it is a Baldor, 230V, single phase, 184T frame, 2 HP, 1750 RPM, Class B insulation, capacitor start, explosion proof. Motor reads open, phase to phase with ordinary ohmmeter (Capacitor does not charge up). Motor also reads grounded on each phase with 500 Volt megger. Temp taken with a temp gun from inside comp room is 150F (65C) at the plenum.
Fan is belt driven. There is no overload protection, just temp protection within the motors themselves. Breaker for two of the fans is 20amps, which is ok. On the third, it is 30amps, which is not ok. Conductors are #10 awg.
The "story" (ahem ...) is that each of the three fan motors in the building take turns "burning up". The latest one sat around in the weather with the pecker head cover off for quite a while. (Don't know if it would matter much as this is a sealed connection box, due to being Class I, Div 2.) So when it finally got wired up, it didn't last long. It was wired up correctly, btw.
So, Class B insulation is rated for 130C. Since the motor will run 40C above ambient, it should be ok up to 90C (195F). Today was cool and damp around 65F. I can see the plenum becoming too hot for the motors, but they are not in the plenum, being a belt system.