I know that most of the time, we run the GEC from the service switch to the grounding collector bus.
I’d like to confirm whether the following scenarios constitute code violations. If so, please let me know the applicable code sections. Thank you.
1. Running the GEC along with the phase conductors and neutral from the SEB to the service switch, and then a single GEC from the service switch to the grounding collector bus.
For example: (1) 600 MCM Cu per phase and neutral with (1) 1/0 Cu GEC in a 4" conduit from the SEB to a 400A service switch. Then, a separate 1/0 Cu GEC runs from the 400A service switch to the grounding collector bus.
Question: Would it be a violation to run the 1/0 Cu GEC in the same conduit as the service conductors?
2. In another case, I have a 4000A service switchboard. From this switchboard, I run a 3/0 Cu GEC to the grounding collector bus. Then, a tap section in the switchboard feeds a 400A service switch using (1) 600 MCM Cu per phase and neutral with a 1/0 Cu GEC in a 4" conduit. The 1/0 Cu GEC is connected to the ground bus inside the 4000A switchboard. There is no additional GEC from the 400A service switch to the grounding collector bus.
Question: Is this setup acceptable per code?
3. Same scenario as Question 2, but with an additional 1/0 Cu GEC run from the 400A service switch to the grounding collector bus.
Question: Would this be code-compliant as well?
I’d like to confirm whether the following scenarios constitute code violations. If so, please let me know the applicable code sections. Thank you.
1. Running the GEC along with the phase conductors and neutral from the SEB to the service switch, and then a single GEC from the service switch to the grounding collector bus.
For example: (1) 600 MCM Cu per phase and neutral with (1) 1/0 Cu GEC in a 4" conduit from the SEB to a 400A service switch. Then, a separate 1/0 Cu GEC runs from the 400A service switch to the grounding collector bus.
Question: Would it be a violation to run the 1/0 Cu GEC in the same conduit as the service conductors?
2. In another case, I have a 4000A service switchboard. From this switchboard, I run a 3/0 Cu GEC to the grounding collector bus. Then, a tap section in the switchboard feeds a 400A service switch using (1) 600 MCM Cu per phase and neutral with a 1/0 Cu GEC in a 4" conduit. The 1/0 Cu GEC is connected to the ground bus inside the 4000A switchboard. There is no additional GEC from the 400A service switch to the grounding collector bus.
Question: Is this setup acceptable per code?
3. Same scenario as Question 2, but with an additional 1/0 Cu GEC run from the 400A service switch to the grounding collector bus.
Question: Would this be code-compliant as well?