Ok. Per that specific information it would be U.F. Cable inside a conduit.Possibly. We could never know what voids any warranty. If the instructions dictate what is to be installed, I would insall it. JMHO
Ro
Weird. The last hot tub I hooked up required #6 copper. Hots, neutral and ground.Ok. Per that specific information it would be U.F. Cable inside a conduit.
If they say #6 for grounded and ungrounded, then I will run that. But when they say #6 for an EGC, I refuse as the #6 would not add one iota to the safety of the EGC when the NEC says #10 is all that is required.If the listing and instructions call for #6 it technically is part of the code. If something happens how do you explain it to the judge?
1. I did it to save money because I know more than the MFG.
or
2. I did everything to code and the instruction manual.
If you don't even own the tool they for sure will win this argument but I've never had a failure either.The thing is they’ll get out of warranty claims no matter what and just cause you torque it doesn’t mean they don’t come back and say well it was loose or over tight. You’d have to be out there when they’re doing their inspection of the units.
Just corporate greed
Know a GC that does roofing as well, and on the 50yr shingles the mfg. companies will always refuse to honor the warranty always claim installation error, even if you can show that their specs say x# nails within xx specified spaces and into xx sub-straight and xx underlayment, and that they complied with every one.The thing is they’ll get out of warranty claims no matter what
Around here there is usually insurance claims from storm damage before manufacturer warranty would apply. Manufacturer warranty doesn't cover such damages in most cases they are just rated to be able to handle so many years of UV exposure and moderate weather conditions.Know a GC that does roofing as well, and on the 50yr shingles the mfg. companies will always refuse to honor the warranty always claim installation error, even if you can show that their specs say x# nails within xx specified spaces and into xx sub-straight and xx underlayment, and that they complied with every one.
Light bulb failed?, not covered under warranty, you must have obviously screwed it in wrong.
There’s no reason for the EGC increase. They’re just morons. I’ve asked them before and could give a straight answer. There’s other Hot Tub manufacturers that do it according to the NEC everything’s kosher it’s just some prima donna dictating that.They probably want a #6 EGC because they feel (right or wrong) that the larger size is more robust and resistant to physical damage.
Same with an GEC on a 100 amp service where I sometimes use #4. #8 needs protection, #6 needs protection if subject to damage #4 not so much.
With all the issues you can have with pools and hot tubs (some electricians want nothing to do with them) and the liability why would someone cut corners on a HT or pool?
MFG. listing as 6/3 they are suggesting NM or UF as the 60o #6 is 55A.Electrical requirements for an outdoor hot tub state the following:
6/3 copper wire with ground in conduit.
This unit requires a 50 Amp circuit.
Would using #8 THWN Hot/ Hot/ Neutral with # 10 E.G. (single conductor) from the disconnect void any warranty?