How long have they been separating the grounds and neutrals in a subpanel? When did it come into the code?
Unless they're in separate structures a 100 years ago?
I believe that before 2008 you were allowed to run a separate ground if you wanted to. I vaguely remember doing a job and being turned down for running an equipment grounding conductor to a separate structure. I appealed, he checked, and all was good.In the same building, forever, in a detached building, since around the 2008 code.
It was decades before that. This is from earliest digital version that I have and this if from the 1965 NEC.1986. That's when sec. 250 really changed everything. I just finished a grocery store build that had main panels from the 1980s and had all neutrals and grounds bonded throughout sub panels.
I also dug this up from the 1937 NEC:250-61. Grounding Equipment to Circuit Conductor.
The grounded service conductor on the supply side of the service disconnecting means may be used for grounding meter housing and service equipment and metallic enclosures and guards. The grounded circuit conductor on the load side of the service disconnecting means shall not be used for grounding equipment, cable armor, or metal raceways except as provided in Section 250-57 (b-4), and in Section 250-60.
2562. Grounding equipment to Circuit Conductor Prohibited. The grounded circuit conductor of an interior wiring system shall not be used for grounding equipment, cable armor, or metal raceway, except by special permission in sub-paragraph 2559-c.
ok wow. Didn't know it went that far back.It was decades before that. This is from earliest digital version that I have and this if from the 1965 NEC.
No. EMT has always been allowed as an Equipment Ground.Interesting. Maybe the '84 NEC removed the EMT as qualified ground? I was 13 then so I'm not sure. But I was wiring homes with my Dad.
So a 1/2" run of EMT servicing a 1 hp motor (120vac, 20A circuit, #12 THHN) with no ground wire still is legal? That's what I'm saying.No. EMT has always been allowed as an Equipment Ground.
Yes. All sizes of EMT are a listed EGC. The 1/2" EMT will likely have a lower impedance than the #12 EGC.So a 1/2" run of EMT servicing a 1 hp motor (120vac, 20A circuit, #12 THHN) with no ground wire still is legal? That's what I'm saying.
250.118 Types of Equipment Grounding Conductors.
The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
(1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4)Electrical metallic tubing.
(5)Listed flexible metal conduit meeting all the following conditions:
a. The conduit is terminated in listed fittings.
b. The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. The size of the conduit does not exceed metric designator 35 (trade size 11∕ 4).
d. The combined length of flexible metal conduit, flexible metallic tubing, and liquidtight flexible metal conduit in the same effective ground-fault current path does not exceed 1.8 m (6 ft).
e.If used to connect equipment where flexibility is necessary to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, a wire-type equipment grounding conductor shall be installed.
(6)Listed liquidtight flexible metal conduit meeting all the following conditions:
b. For metric designators 12 through 16 (trade sizes 3∕ 8 through 1∕ 2), the circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. For metric designators 21 through 35 (trade sizes 3∕ 4 through 11∕ 4), the circuit conductors contained in the conduit are protected by overcurrent devices rated not more than 60 amperes and there is no flexible
metal conduit, flexible metallic tubing, or liquidtight flexible metal conduit in metric designators 12 through 16 (trade sizes 3∕ 8 through 1∕ 2) in the effective ground-fault current path.
e. If used to connect equipment where flexibility is necessary to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, a wire-type equipment grounding conductor shall be installed.
(7)Flexible metallic tubing where the tubing is terminated in listed fittings and meeting the following conditions:
a. The circuit conductors contained in the tubing are protected by overcurrent devices rated at 20 amperes or less.
b. The combined length of flexible metal conduit, flexible metallic tubing, and liquidtight flexible metal conduit in the same effective ground-fault current path does not exceed 1.8 m (6 ft).
(8)Armor of Type AC cable as provided in 320.108.
(9)The copper sheath of mineral-insulated, metal-sheathed cable Type MI.
(10)Type MC cable that provides an effective ground-fault current path in accordance with one or more of the following:
a. It contains an insulated or uninsulated equipment grounding conductor in compliance with 250.118(1).
b. The combined metallic sheath and uninsulated equipment grounding/bonding conductor of interlocked metal tape–type MC cable that is listed and identified as an equipment grounding conductor
c. The metallic sheath or the combined metallic sheath and equipment grounding conductors of the smooth or corrugated tube-type MC cable that is listed and identified as an equipment grounding conductor
(11)Cable trays as permitted in 392.10 and 392.60.
(12)Cablebus framework as permitted in 370.60(1).
(13)Other listed electrically continuous metal raceways and listed auxiliary gutters.
(14)Surface metal raceways listed for grounding.
Informational Note: For a definition of effective ground-fault current path, see Article 100.
There is no rule that says EGC has to be insulated. There is a rule that says you can't use 12AWG EGC on a 30A circuit.One of my guys got called out on inspection using bare copper wire as GEC (he stripped a 20' section of ROMEX and pulled that into EMT). Inspection said no bare copper GEC allowed. I think he was trying to bust him for using ROMEX that had been stripped. It was a 30A 240v run to an electric water heater.