Hello gents,
I am an IBEW journeyman/foreman, and I attend a church in south Orlando, FL that is currently leasing a crappy commercial space with even crappier Federal Pacific panels. Recently, I was told that the (2) AC rooftop units were not working, and that the display on both thermostats corresponding to them inside were dead. An HVAC guy came by to look at the units, and he said the problem was that the main breaker on the panel they were fed from would not properly reset. When I was asked to go look at it to see if there was at least a temporary solution for the weekend services (it was last Friday), this is what I saw after taking the panel cover off (check out C phase):
I locked out the 125A feeder breaker from the main panel outside which feeds the 125A main breaker in *this* panel, and decided that I'd better opt out of touching it as far as repairs were concerned; I am licensed and know how to do the work, but I don't have my own bonded an insured business, so I figured the landlord should be dealing with this. This was strongly encouraged by a couple of my elders in the trade as well. The landord is clearly cheap and sleazy, given the state that he left the building in when we moved in, and the fact that he avoids repairing or paying for anything like the plague. So I'd certainly rather not work with someone like that unless I have the proper protection in place.
Later on, I get a call from the landlord's maintenance guy, asking me about the situation, and why the main panel feeder breaker was locked out. I explained everything to him, and told him it was a miracle that the building didn't burn down. As soon as he approached the inside panel he could smell it.
So with that, I heard over the weekend that the landlord would be having someone take care of the panel swap this week. I found out today (Monday) that this same maintenance guy I spoke to over the phone previously is in fact the one who is going to be doing the panel swap. He had some understanding of electrical, but definitely didn't seem to have enough knowledge to be a competent electrician. He asked me if the replacement panel would also need a 125A main disconnect breaker like the existing one. I told him no, but that the panel itself needed to be rated for at least 125A. I told him that the subfeeds needed to also be replaced, and he told me that he planned to leave subfeed the wires and just swap the panel out. I told him that the subfeed wires absolutely needed to be replaced because due to the heat (especially on C phase), they were now compromised. He said that was going to be a problem because the landlord was definitely not going to want to pay for that. I told him, "well, he needs to, because that's a hazard and those feeds can't be trusted anymore." He asked me how to size replacement feeds, so I told him what he would need for everything in copper THHN. That's the last I spoke to him, and have yet to receive any updates.
I don't know what the status is at the moment, but I'm prepared to potentially encounter a few different things:
A. The landlord refused to replace the subfeeds altogether
B. The maintenance guy replaces the subfeeds & panel, but does a subpar job and there are code violations within the install
C. I keep getting asked about how to do a proper install even though I'm not being paid for this
Basically, we're in a situation where we may end up having to take legal action. Fortunately I can identify code violations, and we have two lawyers who are members of this parish. I'm wondering if any of you have dealt with something like this before? Any advice on handling a situation like this? This is the first time I've dealt with this kind of thing, and I want to make sure we play our cards right. Any advice would be greatly appreciated.
Thank you,
-Jesse
So the landlird moved out and you moved in and you want legal advice?
Call a electrician or move out. Dont touch anything...
Still need a electrical contractor...
'Specialy if your going litigation.
Yeah, or at least the work needs to be done up to the standard of the code. I'm thinking that the next step should be to assess the work that was actually done and go from there.
I would also call the local AHJ and ask for advice. They might be able to open a code case against the owner. Or just get a contractor licensed friend to help you do the panel replacement and when it is time to move out, take it with you and put the old one back in.
Since the neutral isn't being used, perhaps repurpose it for phase C and cut back and splice onto the burnt C phase wire to feed the neutral bus. Need to move the white tape then too.
There’s no way I’d put the old one back in. You’ll get blamed for it by the next tenant.
You have the photos and they probably are talking to the landlord about fixing it. That is all date stamped and paper trail. It would be put on the landlord to repair. They would have a hard time pinning it on the church since the land lord was notified and neglected to fix it. You can take your equipment when you leave. Whether or not the code lets you reinstall or reuse it at a new location is a different issue. lol
Or the Fire Marshall...
If something goes south, the lawyers will go after everybody who touched it.
Yes, it may be the case that the lease is "as is"..I know it is for some things, but I don't know 100% what the terms are for the electrical/AC functioning and being up to code. I'll have to look into that part in more detail.
Update: the maintenance guy changed the panel out today. The landlord told him to keep the subfeeds, that they were fine (even though the insulation on C phase is visibly scorched). I also noticed just by looking at the pictures again that those subfeeds are only 1/0 aluminum XHHW-2, which have a 120A max ampacity @75⁰C, fed from a 125A breaker. He also installed 70A breakers instead of the 80A ones which previously fed the AC rooftop units. Tomorrow I'm going to take the cover off of the panels to look at his wiring, and also check out the rooftop units to see what the amperage is for them, and if their feeds are sized correctly.
480 volts, compromised aluminum conductors, place of assembly, panel installed by a handyman,,,,,,,,
Do you ever watch the Fascinating Horror Youtube channel? It's pretty good
Yeah
Fortunately it's 208, not 480, but still. Let's hope our church doesn't end up being the next story on that channel, haha.