Sjohns4
- Huntington WV
- Engineer
I’m looking at an existing installation. We have a 480v Wye service to the building. Basically the HVAC and sewer pump are 480/3, then we have a 120/208 transformer for outlets, and two separate 480V sub panels full of 1-pole light circuits. There as a 3-pole manual transfer switch with generator conductors ran from an enclosure with lugs for a generator connection. However I’m just seeing 3 phase conductors and the EGC lugs.
Seems to me we’re missing the neutral??
Pretty sure there has never been a generator hooked up.
Is there a scenario where only hooking up 3 phase conductors and the EGC to the generator will allow the lights & transformer (if it’s Wye primary) to work correctly?
Thanks,
Mike