- Tennessee NEC:2017
- Semi-Retired Electrician
Why would you do that when the cord on the appliance can just be changed to a 3-wire?Can someone use 406.4(D) to put in a 4-prong range or dryer receptacle on a GFCI breaker?
Yes thats why I find 406.4(D) inconstant with its GFCI requirement, it makes no difference if the receptacle a 2-prong or a 3-prong with no EGC connected.Case 4 definitely stands out to me because it could potentially provide some good protection in the absence of an EGC.
Yes And the most common case of case 9 is docks, swimming pools and spa/hot tubs with missing GFCI/RCD or no-GFCI/RCD protection.Case 9 is particularly interesting too because it seems as though the combination of having an EGC and not having a GFCI can lead to an even greater shock hazard (therefore adding more value to the addition of a GFCI - Case 10).
In a pool or a spa/hot tube it should not be possible to touch the hot conductor. Docks are a different story because we run power out on the dock.Yes And the most common case of case 9 is docks, swimming pools and spa/hot tubs with missing GFCI/RCD or no-GFCI/RCD protection.
That is correct. A GFCI device does depend on the source being supplied from a grounded system to function.. . . I said a GFCI does NOT need an EGC to operate.
I am thinking of real pools...there is nothing in the world that prevents idiots from being idiots.
Well, it would still serve to trip if one of the downstream circuit conductors had a high impedance inadvertent connection to a line conductor that is upstream of the GFCI. Not very likely.In theory, a GFCI serves no purpose in a non-grounded system, as no substantial current would flow to earth.
Thats what PV system GFCI's do right?Well, it would still serve to trip if one of the downstream circuit conductors had a high impedance inadvertent connection to a line conductor that is upstream of the GFCI. Not very likely.
Cheers, Wayne
I actually made a thread on this very topic back in 2018 - I can't believe it's been 7 years since.That is correct. A GFCI device does depend on the source being supplied from a grounded system to function.