Why would you do that when the cord on the appliance can just be changed to a 3-wire?Can someone use 406.4(D) to put in a 4-prong range or dryer receptacle on a GFCI breaker?
Why would you do that when the cord on the appliance can just be changed to a 3-wire?Can someone use 406.4(D) to put in a 4-prong range or dryer receptacle on a GFCI breaker?
Yes thats why I find 406.4(D) inconstant with its GFCI requirement, it makes no difference if the receptacle a 2-prong or a 3-prong with no EGC connected.Case 4 definitely stands out to me because it could potentially provide some good protection in the absence of an EGC.
Yes And the most common case of case 9 is docks, swimming pools and spa/hot tubs with missing GFCI/RCD or no-GFCI/RCD protection.Case 9 is particularly interesting too because it seems as though the combination of having an EGC and not having a GFCI can lead to an even greater shock hazard (therefore adding more value to the addition of a GFCI - Case 10).
In a pool or a spa/hot tube it should not be possible to touch the hot conductor. Docks are a different story because we run power out on the dock.Yes And the most common case of case 9 is docks, swimming pools and spa/hot tubs with missing GFCI/RCD or no-GFCI/RCD protection.
That is correct. A GFCI device does depend on the source being supplied from a grounded system to function.. . . I said a GFCI does NOT need an EGC to operate.