Are you sure it is NM cable and not SE cable/conductors?Terminating 2 existing 3 wire NM cables in a newly installed residential sub panel. One for range one for clothes dryer.
I would say they should terminate on the neutral bar and not the equipment ground bar.
Is that correct.
Thanks
The 3 wire range and dryer circuits were only allowed to the main panel, not a sub-panel. If it's now a sub-panel they need to be upgraded to 4 wire.Terminating 2 existing 3 wire NM cables in a newly installed residential sub panel. One for range one for clothes dryer.
I would say they should terminate on the neutral bar and not the equipment ground bar.
Is that correct.
Thanks
They were allowed if the grounded conductor was insulated. The grounding conductor in NM cable was never permitted to be used as a grounded conductor no matter where the circuit originated.The 3 wire range and dryer circuits were only allowed to the main panel, not a sub-panel. If it's now a sub-panel they need to be upgraded to 4 wire.
I stand corrected. The range is SE cable.Are you sure it is NM cable and not SE cable/conductors?
As for the EM disconnect, you can label it "emergency disconnect, not service" and not have to run a 4-wire.
Panel needs to be 4 wire since I’m adding the Emergency Disconnect
Sounds like after 2026 NEC there must be a service disconnect on outside and run to the inside is always going to be considered a feeder. Basically no more "emergency disconnect-not service equipment".It can remain 3 wire after the Em Disco