480v high leg motor issue

journeyman0217

Senior Member
Location
Tennessee
Occupation
Electrician
i am troubleshooting a three phase 480 motor with voltage issues that is fed by a high leg system. I dont have to much experience with this set up. Would the configuration of the connections to the motor matter? It is fed by a 3 wire 480v delta high leg system. i did not think it would matter because it is a 3 phase motor, not single phase.
 
It’s a step up transformer. Service coming in is 240v three phase high leg. Steps it up to feed the motor.
 

Attachments

  • 87803873-DC50-4580-AD18-CD2700DE39D6.jpeg
    87803873-DC50-4580-AD18-CD2700DE39D6.jpeg
    248.8 KB · Views: 15
OP, That is a Delta to Delta transformer. You would need to bond the secondary at some point to get a reliable reference voltage to ground.
I don't think that transformer is being used correctly if it is step-up as you suggest. It may not have anything to do with your problem though.
Only if the center of the L1-L3 winding was bonded to “ground.” Does the winding even have a center tap?
No center tap.
 
Only if the center of the L1-L3 winding was bonded to “ground.” Does the winding even have a center tap?
It is a delta-delta transformer and has no center tap according to posted nameplate. there are voltage adjustment taps on the high voltage side. If OP is having low voltage issues the tap being used could possibly come into play. Being reverse fed situation he probably should use one of the mid range taps though.
 