That Man
Senior Member
- Location
- California, United States
- Occupation
- Electrical Designer
Running 350KCMIL TC, and the NEC states that the ground wire for for a 350 should be 1/0AWG, but the Houston 154 TC spec lists an integral ground wire sized at 3AWG. This makes it seem like I have to run an extra ground conductor, which luckily is 1/0 and so it also TC rated. But if I needed to run say, a 250KCMIL, I'd still have to run a 1/0 ground. What's the point of the integral ground if it's too small? What am I missing?