That Man
Senior Member
- Location
 - California, United States
 
- Occupation
 - Electrical Designer
 
Running 350KCMIL TC, and the NEC states that the ground wire for for a 350 should be 1/0AWG, but the Houston 154 TC spec lists an integral ground wire sized at 3AWG.  This makes it seem like I have to run an extra ground conductor, which luckily is 1/0 and so it also TC rated.  But if I needed to run say, a 250KCMIL, I'd still have to run a 1/0 ground.  What's the point of the integral ground if it's too small?  What am I missing?
	
		
			
		
		
	
				
			
				