Situation: Mechanical engineer sent a cut sheet for a temporary chiller. Voltage, load calc, and OCP all checked to be compatible. The cut sheet says the SCCR is 5kA. I ran an available fault current calculation and the result was over 12kA. I went to my mechanical engineer to discuss this with him and he said that no electrical engineer in his 25 years has ever mentioned a concern for SCCR.
Do I have a valid point telling him the SCCR is underrated for the electrical condition, or am I misunderstanding SCCR vs AFC?
Note: I am not talking about the AIC rating.
Do I have a valid point telling him the SCCR is underrated for the electrical condition, or am I misunderstanding SCCR vs AFC?
Note: I am not talking about the AIC rating.