Situation:  Mechanical engineer sent a cut sheet for a temporary chiller.  Voltage, load calc, and OCP all checked to be compatible.  The cut sheet says the SCCR is 5kA.  I ran an available fault current calculation and the result was over 12kA.  I went to my mechanical engineer to discuss this with him and he said that no electrical engineer in his 25 years has ever mentioned a concern for SCCR.  
Do I have a valid point telling him the SCCR is underrated for the electrical condition, or am I misunderstanding SCCR vs AFC?
Note: I am not talking about the AIC rating.
	
		
			
		
		
	
				
			Do I have a valid point telling him the SCCR is underrated for the electrical condition, or am I misunderstanding SCCR vs AFC?
Note: I am not talking about the AIC rating.
				