Disconnect ground first?

Location
Los Angeles
Occupation
C-10
What are your thoughts, if your in a situation where you have to work live, about disconnecting the ground from a receptacle first. Of course generally first to make, last to break and all that but If you’re holding the yoke in one hand and unscrewing the hot wire with a screwdriver in the other, ungrounding the yoke might lower the chance of current passing through the chest in the event of accidentally touching the hot terminal, it'd seek ground through feet or another path or maybe not at all if you yourself are ungrounded. Any thoughts on this approach? What other risks may be more likely to happen by disconnecting the ground first?
 
Any thoughts on this approach?
Yes IMO it's safer for the reason you've mentioned. With the EGC disconnected all of the metal parts of the receptacle (yoke, screws, etc.) are no longer a path for the current to travel if you accidentally touch the ungrounded conductor. You can hold the device in your hand and as long as you're not grounded some other way or are touching the neutral you won't become part of the current path when contacting the hot leg. Although I would always disconnect the EGC first I would wear gloves when doing so.
 
Last edited:
I would always be wearing hot gloves for this and would disconnect the EGC first to lessen the risk of arc.

Mark
 
Here is what artificial unintelligence says 🤣🤣🤣🙄🙄🤬

First to make, last to break" refers to the safety rule for connecting and disconnecting electrical circuits, which dictates that the ground wire should be the first to be connected and the last to be disconnected. This order ensures a continuous ground path is established before current can flow, providing a crucial safety measure to protect against shocks or equipment damage by offering an alternate path for fault current away from the person making the connection.
Why connect the ground first?

Safety from Shocks:
If a hot wire is accidentally energized, the ground connection provides an immediate path for fault current to flow to the earth, rather than through a person.
 
Safety from Shocks:
If a hot wire is accidentally energized, the ground connection provides an immediate path for fault current to flow to the earth, rather than through a person
Yup AI isn't there yet. The first make last break refers to a plug where the ground pin is longer than the hot and the neutral pins.
 
In a panel I connect ground first so I don't have a long bare piece of copper just waiting to get knocked into something hot
 
Yes IMO it's safer for the reason you've mentioned. With the EGC disconnected all of the metal parts of the receptacle (yoke, screws, etc.) are no longer a path for the current to travel if you accidentally touch the ungrounded conductor. You can hold the device in your hand and as long as you're not grounded some other way or are touching the neutral you won't become part of the current path when contacting the hot leg. Although I would always disconnect the EGC first I would wear gloves when doing so.
So would you hook it back up, hot first?
 
So would you hook it back up, hot first?
Why would it be hot if you're installing it in the panel?
If installing a new circuit, it doesn't matter the order you put the conductors in. However, as mentioned, the ground and neutral is in the back and easiest to install first.
Technically, you should have the main off.
 
Why would it be hot if you're installing it in the panel?
If installing a new circuit, it doesn't matter the order you put the conductors in. However, as mentioned, the ground and neutral is in the back and easiest to install first.
Technically, you should have the main off.
Sorry, I wasn’t clear. I was referring to the receptacle. If one chooses to disconnect ground first on a hot receptacle, the question is do they chose to hook up hot first when connecting receptacle
 