- Illinois
- retired electrician
The permission to mark the outside disconnect as "emergency disconnect, not service equipment" is what triggered all of the issues. Multiple bonding points are permitted on the line side of the service equipment.For some reason my downloaded pdf copy of the 2023 code stops at 230.84 so I was wondering what you were talking about. I had to go back to the 2020 for 230.85. Not sure if anything changed but I'm not seeing anything that would prevent a disconnect switch after the meter. Just the normal bonding of service equipment. The neutral would carry through to the main panel and land on the neutral bar.
Better yet, like I said above incorporate it into the meter enclosure. Then it is out of the NECs jurisdiction. We have bypass meter enclosures with switch contacts, what's the problem?
-Hal
Anything that is not the service disconnect, will permit those multiple bonding points.
Putting it into the meter enclosure would take the cooperation of the utilities. Most utilities have a list of meter enclosures that they will accept. Also, what authority could require this disconnect to be part of the meter enclosure?
A lever bypass meter enclosure does not have switch contacts that will cut off the supply of the power. They do two things, loosen the grip of the meter socket to the meter blades, and to bypass the meter...that is let the power flow when the meter is removed.