Okay the you don’t need to run 60 amp—— you have feeders you can just run 30 amps circuits if that’s all you need.The meterpak takes 30A QO’s, but I think 230.79 or something similar is where the inspector is coming from. I didn’t feel like arguing with him as he’s pretty knowledgeable, seemed to be an electrical contractor in the past. There’s already a main fused disconnect for all 11 meters.
The rating of the discount has to be not less than 60 amp not the circuit—- read the section— he wrong
Always argue with them they know just as much as us and that nothing- your right there wrong is my motto lol