Exposed NM 6/3 and 10/3

The meterpak takes 30A QO’s, but I think 230.79 or something similar is where the inspector is coming from. I didn’t feel like arguing with him as he’s pretty knowledgeable, seemed to be an electrical contractor in the past. There’s already a main fused disconnect for all 11 meters.
Okay the you don’t need to run 60 amp—— you have feeders you can just run 30 amps circuits if that’s all you need.
The rating of the discount has to be not less than 60 amp not the circuit—- read the section— he wrong

Always argue with them they know just as much as us and that nothing- your right there wrong is my motto lol
 
Okay the you don’t need to run 60 amp—— you have feeders you can just run 30 amps circuits if that’s all you need.
The rating of the discount has to be not less than 60 amp not the circuit—- read the section— he wrong

Always argue with them they know just as much as us and that nothing- your right there wrong is my motto lol
I’m gonna ask him about this today when he comes. I’m already scheduled to have to turn off the whole building in order to swap power to these disconnects so too late now, but I always like to know for a fact what the rule is
 
I’m gonna ask him about this today when he comes. I’m already scheduled to have to turn off the whole building in order to swap power to these disconnects so too late now, but I always like to know for a fact what the rule is
Read it yourself interpreting yourself half that book is gray area that you can flip your way you just gotta know how to phrase it. Whatever I can do to stick it to someone. I should’ve been a lawyer. I got that mindset.
 
Read it yourself interpreting yourself half that book is gray area that you can flip your way you just gotta know how to phrase it. Whatever I can do to stick it to someone. I should’ve been a lawyer. I got that mindset.
This has really got me thinking. So even though each breaker is the first disconnect after the meter, so technically each one seems like it is a “service” disconnect, it really isn’t? They’re just main disconnects and each wire is just a sub?
 