I had not considered this but you are correctNotable that the he says, "All GFCI outlets" not GFCI protected outlets. If the definition of outlet were added, it would require you putting stickers on light fixtures and bathroom fans, the way he is enforcing it.
I wired a residential elevator shaft that required GFCI protected service receptacles at the top and bottom of the shaft. So I used a GFCI breaker and wired standard receptacles in the shaft.They should have provided you with a code reference. 210.63(A) makes no mention of the GFCI protection reset being at the device so unless this is a local code the NEC allows protection at the circuit breaker.
The inspector was correct, see 620.85I wired a residential elevator shaft that required GFCI protected service receptacles at the top and bottom of the shaft. So I used a GFCI breaker and wired standard receptacles in the shaft.
Elevator inspector came out and insisted on GFCI receptacles at each location instead of a single GFCI breaker in the panel.
I asked the inspector to site a code reference but the elevator installer shut me down and told me to just change it. The inspector was about 75 years old, could barely see or walk onto the job site. He had no business being an inspector, the elevator installer agreed with me on that at least. LOL.
I would presume the thinking in an elevator shaft a tripping GFCI would introduce an additional hazard if needed to leave to go to a central panel location to return power. I know most of us use battery powered service lights now but part of the concern would be loss of lighting in the elevator shaft particularly when working at the top.I wired a residential elevator shaft that required GFCI protected service receptacles at the top and bottom of the shaft. So I used a GFCI breaker and wired standard receptacles in the shaft.
What code cycle you looking at Don't see 420.85? I do see the requirement for GFCI "receptacle" in the 2023 @ 620.6(A) TYPO EditThe inspector was correct, see 620.85
typo, was looking for 620.85 NFPA Link jumps from 620.84 to 620.91I posted 620.85, not 420
It was 620.85 in earlier cycles but moved in 2020 to 620.6.typo, was looking for 620.85
It was relocated in the 2023 code to the section that you cited in post 27typo, was looking for 620.85 NFPA Link jumps from 620.84 to 620.91
Occasionally the inspector gets it right, as opposed to what many out there think.The inspector was correct, see 620.85
Only occasionally?????? Thanks for your confidence in inspectors!Occasionally the inspector gets it right, as opposed to what many out there think.
Sorry, forgot the sarcasm emoji. We do try, with over a 1000 pages and changes every three years sometimes have to take a second look, but also open to legitimate questions when presented with "what about this section". I tell the guys if you disagree give me a counter code reference.Only occasionally?????? Thanks for your confidence in inspectors!
Ron