Hi, I'm doing some electrical homework and ran across this question.
"The hot water for the heating system for a small factory is supplied by a single boiler. The boiler is located in a small building separate from the factory. The power supplied to the boiler is 240V single-phase without a neutral conductor. At the present time, the small building housing the boiler has no inside lighting. The business owner desires that four 100W lamps be installed inside the building. All lamps are to be connected to a single switch. The lamps are to be connected to the present 240V service inside the building. How would you accomplish this task? Explain your answer."
Here's what I got this far, I don't think I'm right but I can't figure out where I went wrong:
240V power supply 4(100W) = 400W lamps wired to single switch
Wire all lamps in parallel with the switch so that the switch turns on all lights but if one light burns out, it won’t affect the other lights. Wire the switch in series with the 240V power supply.
I = 100W/240V = 0.417A per bulb. Total current is summed in parallel circuits.
0.417A * 4 = 1.668A needed through switch into lights.
240V/ 0.417A = 575.54ohms resistance per bulb.
Rtotal= 1/ (1/575.54 + 1/575.54 + 1/575.54 + 1/575.54)
Total resistance of bulbs using reciprocal formula = 143.885ohms
SQRT (P X R) = V
SQRT ( 143.885 * 100 ) = 119.952V
240V – 119.952 = 120.048V drop needed.
P = (1202/36.029) = 399.678 rating for resistor.
R = (120.0482 / 400W ) = 36.029 ohms resistor needed to add with 400W power rating.
So the major issue I've been having is I can't figure out why I'm wrong, I know I am but I can't figure out how to think about this issue differently.
Any advice is helpful. Thanks.
"The hot water for the heating system for a small factory is supplied by a single boiler. The boiler is located in a small building separate from the factory. The power supplied to the boiler is 240V single-phase without a neutral conductor. At the present time, the small building housing the boiler has no inside lighting. The business owner desires that four 100W lamps be installed inside the building. All lamps are to be connected to a single switch. The lamps are to be connected to the present 240V service inside the building. How would you accomplish this task? Explain your answer."
Here's what I got this far, I don't think I'm right but I can't figure out where I went wrong:
240V power supply 4(100W) = 400W lamps wired to single switch
Wire all lamps in parallel with the switch so that the switch turns on all lights but if one light burns out, it won’t affect the other lights. Wire the switch in series with the 240V power supply.
I = 100W/240V = 0.417A per bulb. Total current is summed in parallel circuits.
0.417A * 4 = 1.668A needed through switch into lights.
240V/ 0.417A = 575.54ohms resistance per bulb.
Rtotal= 1/ (1/575.54 + 1/575.54 + 1/575.54 + 1/575.54)
Total resistance of bulbs using reciprocal formula = 143.885ohms
SQRT (P X R) = V
SQRT ( 143.885 * 100 ) = 119.952V
240V – 119.952 = 120.048V drop needed.
P = (1202/36.029) = 399.678 rating for resistor.
R = (120.0482 / 400W ) = 36.029 ohms resistor needed to add with 400W power rating.
So the major issue I've been having is I can't figure out why I'm wrong, I know I am but I can't figure out how to think about this issue differently.
Any advice is helpful. Thanks.