Hey folks,
Wanted to update you with the latest.
The problem continues. Operators have let me know that the "single phasing" of the vfds has spread to 2 other brands of VFDs. I went there Tuesday and the voltage is the following:
AB 247V
AC 246V
BC 228V
This is an imbalance of 5.1%
I come back on Friday to shut the building down to get a voltage reading from the pole without the building load and voltage is
AB 245V
AC 244V
BC 243V
Imbalance of 0.5%
Turn power back on
AB 243V
AC 242V
BC 240V
Imbalance 0.7%
I check a VFD and I still have it single phasing on input. Zero current on A phase.
I decide to let some time lapse and recheck. About an hour and recheck a couple more times.
AB 243V
AC 241V
BC 239V
Same problem on different VFD
POCO has not been helpful, stating the voltage is within specs.
So with the power off the imbalance goes away, that leads me to suspect the customer is incorrectly loading the bank or you have some hi resistance failing connections. Some photos would help.
When I have fixed this exact problem it was by either moving the loads around or having the POCO close the delta;
Consider there are 4 main types of loads you can have on a typical utility 240 hi-leg delta made from 3 transformers on a pole
(In theory 5 types but I digress)
- 120V loads (two wire),
- 120/240 3-split phase loads (three wire),
- single phase 240 loads (two wire)
- three phase 240 loads (three wire).
Where B is the wild leg;
A-C is the split phase lighting pot,
A-B is a power pot; and B-C is a power pot
the first two kinds of loads
120V loads and 120/240 3-wire split phase loads
are only on the A-C winding so I calculate them differently
Where as the third type, straight 240 single phase loads, can be on any of the pots A-B, A-C, or B-C,
these loads used to be less common but are becoming very common, loads such as server racks or single phase 230V equipment.
The last type 240 three phase loads (the most common) evenly load all three pots.
Now if we eliminate the B-C, pot and make it a open hi-leg delta the kVA rating of the entire bank degrades.
Any non-three phase loads that use both transformers such as single phase 240 loads connected 'B-C' across the open set or the 5th type a 208V load running B-Neutral degrade the kVA rating even more and can cause voltage instability.
I have never seen the 208V L-N done intentionally but I do come across single phase 240 loads on the open set (B-C), moving those loads to the power transformer A-B improves the voltage stability.