Alwayslearningelec
- NJ
- Estimator
What would constitute using the fixture as a raceway? Pulling wires THROUGH it ? If you did not pull wires through it you would have to splice at each end of fixture ...in the fixture?? Or a box at each end?Nothing would prevent it as long as you're not pulling in other circuits and using the fixture as a raceway (unless so marked).
See 410.64(C).What would constitute using the fixture as a raceway? Pulling wires THROUGH it ? If you did not pull wires through it you would have to splice at each end of fixture ...in the fixture?? Or a box at each end?
Yes, aware of that. ThanksYou generally have to keep emergency circuits separate too. Not a fixture that has its own internal battery, but one supplied from a separate branch circuit from a generator and transfer switch.
I only mention due to the "EMB" designation on the 1st fixture.
The short answer is if the fixtures are all of the same switch leg they can be piped in and out.Yes, aware of that. Thanks
Thanks. Can you splice in the fixture?The short answer is if the fixtures are all of the same switch leg they can be piped in and out.
Yes.Thanks. Can you splice in the fixture?